We have several new drinking fountains on GFCI outlets. The GFCIs are tripping regularly.
We replaced one GFCI with a standard outlet for testing. When operating the electric "push to drink" switches, a very brief current spike up to 2A appears on the equipment grounding conductor between the cord and the metal casing. The spike is too fast to see on the digital meter, but the meter catches it with a "max" record function. Measuring voltage between neutral and ground again picks up a brief but definite spike of a volt or two. I get the same kind of spike with the ammeter around the H and N leads, but not if I include H, N, and G.
The event is definitely linked to the operator switches. I wasn't able to tell if the same happens when the cooling fan kicks on, but based on reports of when these are tripping, I think it is probable.
Any ideas what is going on?
We replaced one GFCI with a standard outlet for testing. When operating the electric "push to drink" switches, a very brief current spike up to 2A appears on the equipment grounding conductor between the cord and the metal casing. The spike is too fast to see on the digital meter, but the meter catches it with a "max" record function. Measuring voltage between neutral and ground again picks up a brief but definite spike of a volt or two. I get the same kind of spike with the ammeter around the H and N leads, but not if I include H, N, and G.
The event is definitely linked to the operator switches. I wasn't able to tell if the same happens when the cooling fan kicks on, but based on reports of when these are tripping, I think it is probable.
Any ideas what is going on?