GFCI and lighting circuit

Status
Not open for further replies.

jhrper

Member
Morning fellows. I know that it is permissible to replace a non-grounding type receptacle with a GFCI on a two wire circuit. My question is if you have a two wire circuit that has only lighting and switches can you use a GFCI breaker in the panel to make up for the lack of an equipment ground?
 
Gfci and lighting circuit

Gfci and lighting circuit

That was brought up in a code class I attended. When changing a service entrance from fuses to circuit breakers all ungrounded circits should have gfci protection.

The reason is that a fuse blows faster than a breaker trips, by replacing the fuse to a breaker you are adding to an existing hazard.

any comments?
 
got any NEC code numbers to add to that? I would think lots of trouble in identifying which hots and nutrals go together in an old knob and tube system.
 
GFCI and lighting circuits.

GFCI and lighting circuits.

ACRWC10 A simple test with a voltage tester will identify the polarity of knob and tube wiring. It must be done any time knob and tube is disconnected and reconnected for any reason,reversing the polarity could result in changing the voltage to some outlets from 110 to 240.

jhrper Yes GFCI protection can be used to protect a lighting circuit. A ground fault to a metal light should trip the GFCI breaker. IMO.

Kind of busy at the moment will look NEC section about not adding to existing violations laterif antone still want's it.
 
romeo said:
ACRWC10 A simple test with a voltage tester will identify the polarity of knob and tube wiring. It must be done any time knob and tube is disconnected and reconnected for any reason,reversing the polarity could result in changing the voltage to some outlets from 110 to 240.
Yes, as will the average non-contact tester. My fav is a wiggy and an extension cord plugged into a known-properly-wired receptacle.
 