GFCI at sump&condensate pumps?

Status
Not open for further replies.

ins.GDF

Member
Can single,non GFCI receptacles supply power for sump and HVAC condensate pumps.Both are located in unfinished basements?Would they be considered appliances located in dedicated space?:-?
 
Under the 2008 NEC there are no exceptions for either of those pumps in unfinished basements, crawl spaces or garages.
 
If you're still under the 2005 NEC you can use a single receptacle. Or under the 2008 you can use a 240 volt pump without GFCI protection.
 
peter d said:
But that would involve spending money. ;)

Aren't we all rich ? Everyone is always telling me how much we electricians make.:D
 
acrwc10 said:
Aren't we all rich ? Everyone is always telling me how much we electricians make.:D

Ah but you know you can't measure wealth in dollars and cents. We just love our work.

Now, Peter is money rich because he refuses to buy a GFCI's. I bet he doesn't have 2 ground rods at his house either. :D
 
Dennis Alwon said:
Now, Peter is money rich because he refuses to buy a GFCI's. I bet he doesn't have 2 ground rods at his house either. :D

Peter thinks he is rich because he thinks he is pretty, or is it beautiful?
 
Anybody know why they allow 240 V stuff to not be on GFCIs - like the 240V sump.
And also the same for Arc Fault circuits as well?
 
alfiesauce said:
Anybody know why they allow 240 V stuff to not be on GFCIs - like the 240V sump.
And also the same for Arc Fault circuits as well?

I believe because most appliances that a ho would use is 120v. The GFCI is to protect people not the appliance.
 
alfiesauce said:
Anybody know why they allow 240 V stuff to not be on GFCIs - like the 240V sump.
And also the same for Arc Fault circuits as well?

I don't know but I suspect it is accident statistics.
 
Dennis Alwon said:
Now, Peter is money rich because he refuses to buy a GFCI's. I bet he doesn't have 2 ground rods at his house either. :D

Nope....I can do one better. I have no ground rods at all. How 'bout that?? Just one GEC to the water main. That's it. Oh, and K&T to boot. :D
 
A GFCI trips between 4 -6 mA and above. If the condensate pump trips it, what is the leakage current? 30 mA will cause a fatal shock.
 
tom baker said:
A GFCI trips between 4 -6 mA and above. If the condensate pump trips it, what is the leakage current? 30 mA will cause a fatal shock.

This may be true but would that not be the same for a 220v condensate pump or sump pump. No GFCI is necessary on those.
 