joes_electric
Member
- Location
- Tunkhannock,Pa
- Occupation
- E&I Tech (Retired)
I am testing a Sq-D QO 2 pole GFCI breaker on my bench. If I connect a 5.5 MA load from either hot pole to the breakers neutral or the pigtail neutral, no trip as expected. However if I connect a 6.7 MA load from either hot pole to the breakers neutral, NO TRIP. Connecting the same 6.7 MA load to the pigtail neutral WILL trip the breaker. Why no trip when the load connects to the breakers neutral? I am supplying the breaker with 220 Volts and am using 22 k and 18 k high wattage resistors as my test load. What am I missing here? Thanks...