GFCI breaker for 2 wire non ground receptacles

Status
Not open for further replies.

Bobd59

Member
Location
St.Louis Mo. metro east
Occupation
Electrician
The sellers inspection for my mothers house turned up 3 wire receptacles installed in several rooms at the house. In the bedrooms I just replace the receptacles with the two wire ones. For the living room I tried to add a GFCI breaker in the panel. The thought was in the living room you might be more likely to need a 3 prone outlet. The breaker will not trip. My outlet tester shows no ground at the receptacles. So far I haven't found a problem with the circuit. Pulling new romex with a ground isn't an option since the basement has drywalled ceilings and walls. I tried replacing the breaker with the GFCI breaker I installed for the garage (I know it works) with the same result. I do show 120 at the receptacles with a wiggy. Any ideas, or should I just give up and replace the receptacles. Final inspections coming up soon.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you are using a tester to make it trip it will not work with no equipment grounding conductor. If you push the test button and it trips then that is all you need. That means the device is working properly.

Btw, welcome to the forum
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Bob, a GFCI device does not make an EGC magically appear in the circuit; it merely provides additional protection for loads that would otherwise depend on an EGC for that protection.

A GFCI breaker or receptacle, has access to the circuit's grounded conductor ahead of the current-comparing sensor, which is what it uses with a resistor to mimic a person receiving a shock.

A plug-inGFCI tester has no access to the circuit grounded conductor, so it must use the EGC to mimic a shock. Since your circuit as no EGC, a plug-in tester's button can not mimic a shock.

If you were to add a 3-to-2-wire "cheater" to the tester, plug it in, and connect the green wire or tang to a known ground, the plug-in tester would indeed cause the GFCI breaker to trip.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
And since the 2014 Nec, replacement recpts are required to be TR, AFCI, GFCI. I suspect the AFCI requirement is often overlooked or unkown
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
If you were to add a 3-to-2-wire "cheater" to the tester, plug it in, and connect the green wire or tang to a known ground, the plug-in tester would indeed cause the GFCI breaker to trip.

Which is exactly what you'll need to convince most inspectors of GFCI protection (using their 3-prong tester).

And since the 2014 Nec, replacement recpts are required to be TR, AFCI, GFCI. I suspect the AFCI requirement is often overlooked or unkown

Roger that, unless its an electrical inspector they don't know the difference between a GFCI and AFCI
 