GFCI Breaker for Pool Lights
JPC PE
Myrtle Beach, SC
Does the NEC 2017 require a gfci circuit breaker to be used to feed pool lighting circuit if the lighting system in using a NSI Industries TPX300 pool light transformer?
The TPX300 is a step down transformer 120 primary / 14 v secondary.
680.23 (A) 3. Says GFCI breakers to be used branch circuits supplying luminaires operating at a voltage greater than the low-voltage contact limit.
Looking at the situation from the primary side one would say YES to the GFCI
Looking it from the secondary side one would say NO.
Advise
Thanks
The primary side needs gfci protect however I have never seen gfci protection on the secondary side. We also gfci the line and that's all one can do.
BTw, welcome to the forum
I have never seen a GFCI made for LV. Further, because the LV secondary is prohibited from being grounded (IE it's floating), if it should fault to something there would be no risk.
-Hal
Does it ? The LV limit referred to in the article is 50v I believe; If you have less than that going to the shell of the pool I don’t believe a GFCI is required.
-Hal
interesting, was the intent on purpose?....~RJ~
I'm imagining a step potential applies for water, along with those immersed in it
that said the older industrial ungrounded deltas w/impedance shunts (230.82-4) comes to mind
one leg to ground was no thing....
~S~