nec 555.3 states a marina main over current protection must be gfci protected or individual branch circuits can be gfci
we are rebuilding a major dock and need to update the service & equipment destroyed by hurricane irma
i need a 600 A main breaker service and the manufacture ( Eaton) only has a 3 phase breaker available in 600 a, but there is only 1 phase service available. will this work properly to protect the dock pedestals?
thought about using individual 100 a gfci breakers in the main load center for the pedestals, but they do not make a 100 a gfci breaker either
help thoughts......... thanks