GFCI Breaker Question

Status
Not open for further replies.

dave81

Member
Is there a minimum distance that GFCI breakers can safely operate a load I know that with the receps loaded side shouldn't be further than 90 feet but what about the breaker?
 
Re: GFCI Breaker Question

It all depends on the leakage to ground. For example XHHW-2 is better insulation than THHW and will have less leakage. Assuming the breaker and receptacle are both class A devices there should be no difference in distance.

[ March 03, 2004, 07:58 PM: Message edited by: tom baker ]
 
Re: GFCI Breaker Question

The 90 ft load distance was given to me by the technical support at leviton so its probably pretty close to accurate.
 
Re: GFCI Breaker Question

I believe it is a 100 feet,, I just got done wiring 3 spas, and each schematic said the gfci could be no more than 100 feet.
 
Re: GFCI Breaker Question

I believe that this is a design issue not a code issue.

Look back at Tom's post, he summed it up nicely.

Here is what Square D says about the installation of type QO Class A GFCI Breakers

NOTE: To minimize nuisance
tripping:

? Do not connect circuit breaker to
swimming pool equipment
installed before adoption of the
1965 National Electrical Code.

? Do not connect circuit breaker to
electric ranges or clothes dryers
whose frames are grounded by
connection to a neutral
conductor.

? Do not connect circuit breaker to
more than 250 ft. (76 m) of load
conductor for the total one-way
This quote was taken from a Square D web site, I tried linking to it but it would not work, if you want to see it I will email the address to anyone.

"To minimize nuisance tripping" the way I read that is you may ignore these recommendations but that may result in nuisance tripping.

I have done many jobs that get beyond 250 one way on GFCIs, typically for heat trace circuits on process piping.

IMO, a better design has the GFCI as close to the outlet or equipment it serves but it is not a code requirement to do so.
 