What is more reliable(faster) in tripping, a gfci breaker or actual gfci device? and having both is really double the protection? Heard something at work confused me a bit
You can use both on the same circuit.
Magnetic trip breakers & current limiting fuses can operate faster than GFCI's, if the magnitude of the fault waveform is large enough.
GFCI circuitry also has a trip curve, and the UL specification for Class-A GFCI's disconnect speed is similar to inverse time circuit breakers, not necessarily faster.
What is more reliable(faster) in tripping, a gfci breaker or actual gfci device? and having both is really double the protection? Heard something at work confused me a bit
UL 943 says that Class A GFCIs should have the inverse-time trip curve shown in figure 2 over a leakage current range of 6 to 264 mA, but some manufacturers of lower-priced Class A devices do not implement the curve because it makes the design more complicated, and instead use an instantaneous response that is lower than the quickest response required by the code just to pass testing. The UL curve is the absolute highest time response accepted but it is not restrictive. A device will fail UL testing if it responds to a fault slower than the curve suggests but will pass as long as the response time is less than the curve time. Too-quick response to transient ground-fault currents of low magnitudes will cause nuisance tripping; this is the main reason for not using residential type Class A GFCIs in industrial applications even where the line-to-line voltage is 240 V or lower and the system leakage is less than 6 mA. | |