GFCI Circuit and another dual function circuit in same conduit

T DeNault

Member
Location
New York
Occupation
Electrician
Hello, wired in a swimming pool equipment today and wired a 240 volt GFCI protected circuit for pump, and 120 volt GFCI / AFCI circuit for pool lights and outlet. ( reason for duel function breaker is could not get my hands on just a GFCI single pole breaker CH style for cutler hammer) in same conduit. Is this allowable?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't have the book in front of me but there was a time when the GFCI protected lighting conductors could not be in the same raceway with other conductors.
 

T DeNault

Member
Location
New York
Occupation
Electrician
I don't have the book in front of me but there was a time when the GFCI protected lighting conductors could not be in the same raceway with other conductors.
Hello and thank you for replying. Both circuits and conductors are under GFCI protection, it’s just that the 120 volt has the AFCI protection also. Rest assure my fellow sparks, I will consult my underwriter before inspection. Thank you all.
 

retirede

Senior Member
Location
Illinois
I don't have the book in front of me but there was a time when the GFCI protected lighting conductors could not be in the same raceway with other conductors.

I’d bet it’s a circuit for a pool transformer for low voltage lights - he mentions that it also feeds a receptacle. I didn’t think anybody put 120V lights in a pool any more.
 

T DeNault

Member
Location
New York
Occupation
Electrician
I’d bet it’s a circuit for a pool transformer for low voltage lights - he mentions that it also feeds a receptacle. I didn’t think anybody put 120V lights in a pool any more.
Yes sir you’re correct. Feeds the 12 volt LED driver and then to the code compliant outlet. The 240 volt feeds Pump and chlorine transformer as well the ignition for the gas heater. Both circuits are fed from the panel where the GFCI protection is and the duel function protection all in same conduit.
 

retirede

Senior Member
Location
Illinois
Yes sir you’re correct. Feeds the 12 volt LED driver and then to the code compliant outlet. The 240 volt feeds Pump and chlorine transformer as well the ignition for the gas heater. Both circuits are fed from the panel where the GFCI protection is and the duel function protection all in same conduit.

Sounds like you’re good to go.
 