Good morning all.
I installed three low voltage pool lights (controlled from 3 way switches).
All seemed to be working well.
Got a call back that the breaker is tripping. So. Here it is.
3- lights..
3- deck boxes..
3- 120v to 14v 70va xformers.
The owner reported the tripping and that he was having a tough time setting the color of one of the lights (they cycle through color changes).
I removed the xformer from the circ. for the light he mentioned. the other lights would turn on and off, all seemed fine. Then to clarify if it was if it was the xformer or light I took the "known"
good xformer and put it at that deck box......then after cycling the switches on/off several times...when turned off the breaker
would trip.
I removed the load from 2 of the transformers and removed 2 transformers individually and swapped them and..... the circ would hold than after turning the switch on and off "several"
times it would trip again when turned off. Sometimes after turning them on and off "ones".
One time I went to reset the breaker and it tripped as I reset the breaker with lights off.
I'm thinking the travelers of the 3 ways may be damaged but tripping would be happening when the damaged conductor is energized. And with the 3 ways being in different states
for the most part the lights come on all the time and cycle on and off till turned off that last time when it trips.
So- I'm thinking bad light? bad xformer? nicked conductor? garden gnome?
In trouble shooting, I wound up temping a drop light (120v/60w A lamp) to the lines of one of the deck boxes so I didn't have to keep going back and forth to look into the pool to see if the
lights were on or off.
With the A lamp hooked up, and with the xformers and lights hooked up or not hooked up, the lights in the pool turned on and off and worked every time. 50 or more on and off's from either 3-way on and off...
No problems. BUT.... When I removed the A lamp from the circuit, the lights would trip again.
Currently... I hooked everything back up the way it was and the way it "should be"??.
The 3 ways control a lighting contactor in a control panel so at that location I spliced in the 60w bulb.
All is working fine and the way it is supposed to... lol.. the only issue is everytime the owner turns on his pool lights, a light turns on at the other side of the yard... :- )
Any thoughts why these x formers are tripping the circ when turned "off"?
If I could have assistance with my math...... I believe the fixtures themselves were slightly too large to have two lights on one x former so I'm thinking the fixtures are 40w each.
What would be the load for these three xformer/fixtures on the 120v side?
At the 14v side, would va be based on the 70w x former or the 40w fixture it supplies.
If at 70va .... would the 5 amps transpose proportionately to the 120v side or is 5 amps 5 amps? (been a while)
I can only guess that the load is milli-ampish so the breaker is having nuisance tripping, but putting a real load (like the 60w lamp) is holding the circuit...????
Might this be correct?
My best thought for getting through this (and not have the light at the other end of the yard come on with the pool lights) is to install a resistor at the pool control panel
location. 120v resistor??? What color stripes, what tolerance???
Never saw this before. Any thoughts?
Thank you,
Rich
I installed three low voltage pool lights (controlled from 3 way switches).
All seemed to be working well.
Got a call back that the breaker is tripping. So. Here it is.
3- lights..
3- deck boxes..
3- 120v to 14v 70va xformers.
The owner reported the tripping and that he was having a tough time setting the color of one of the lights (they cycle through color changes).
I removed the xformer from the circ. for the light he mentioned. the other lights would turn on and off, all seemed fine. Then to clarify if it was if it was the xformer or light I took the "known"
good xformer and put it at that deck box......then after cycling the switches on/off several times...when turned off the breaker
would trip.
I removed the load from 2 of the transformers and removed 2 transformers individually and swapped them and..... the circ would hold than after turning the switch on and off "several"
times it would trip again when turned off. Sometimes after turning them on and off "ones".
One time I went to reset the breaker and it tripped as I reset the breaker with lights off.
I'm thinking the travelers of the 3 ways may be damaged but tripping would be happening when the damaged conductor is energized. And with the 3 ways being in different states
for the most part the lights come on all the time and cycle on and off till turned off that last time when it trips.
So- I'm thinking bad light? bad xformer? nicked conductor? garden gnome?
In trouble shooting, I wound up temping a drop light (120v/60w A lamp) to the lines of one of the deck boxes so I didn't have to keep going back and forth to look into the pool to see if the
lights were on or off.
With the A lamp hooked up, and with the xformers and lights hooked up or not hooked up, the lights in the pool turned on and off and worked every time. 50 or more on and off's from either 3-way on and off...
No problems. BUT.... When I removed the A lamp from the circuit, the lights would trip again.
Currently... I hooked everything back up the way it was and the way it "should be"??.
The 3 ways control a lighting contactor in a control panel so at that location I spliced in the 60w bulb.
All is working fine and the way it is supposed to... lol.. the only issue is everytime the owner turns on his pool lights, a light turns on at the other side of the yard... :- )
Any thoughts why these x formers are tripping the circ when turned "off"?
If I could have assistance with my math...... I believe the fixtures themselves were slightly too large to have two lights on one x former so I'm thinking the fixtures are 40w each.
What would be the load for these three xformer/fixtures on the 120v side?
At the 14v side, would va be based on the 70w x former or the 40w fixture it supplies.
If at 70va .... would the 5 amps transpose proportionately to the 120v side or is 5 amps 5 amps? (been a while)
I can only guess that the load is milli-ampish so the breaker is having nuisance tripping, but putting a real load (like the 60w lamp) is holding the circuit...????
Might this be correct?
My best thought for getting through this (and not have the light at the other end of the yard come on with the pool lights) is to install a resistor at the pool control panel
location. 120v resistor??? What color stripes, what tolerance???
Never saw this before. Any thoughts?
Thank you,
Rich