In an attempt to increase my troubleshooting repertoire. What reasons have you found that cause a GFCI circuit breaker or receptacle to trip?
151218-2458 EST
WIMaster:
Fluorescent on turn off may produce a rapid rise (dv/dt) voltage spike from its inductive kick that is capacitively coupled to the SCR gate in the GFCI by a poor board layout.
There have been reports of bath fans doing tripping GFCI on turn on or off. Note there can be switch bounce on closure that causes arcing (the rapid voltage spikes) as well as when the switch is opened. Experimentally I have used an 8' Slimline to randomly trip a Leviton GFCI.
.
A brand new 48" two lamp T8 flour caused a GFCI outlet to trip. So did the next light(same model) we bought.
The light style is a shop light: it hangs from the typical two chains. It is cord and plug connected to an outlet that is on a circuit with GFCI protection provided via another outlet.
First idea was: get a new light but it also caused the problem. Both lights regardless of GFCI caused the fault.
*
Second idea is: We rearranged the circuit and provided a non GFCI source to the light. Supply house doesn't agree there is a problem. I intend to contact ballast mfg to see if they concur. AHJ says the light is non compliant if not able to operate on GFCI.
:?
Reasons I have found for GFCIs tripping
Reverse polarity.
Will reverse polarity trip a GFCI?
It will if one absent mindedly wires a smartlock GFCI reverse polarity then turns the circuit back on. :ashamed1:
Receptacles go bad quite a bit, .....
I have had enough that worked fine after replacing them that unless there is some obvious fault ( bad cord, ect..) I replace the GFI. 99% of the time that fixes it....
Diagnosing bad GFCI recpts is pretty straight forward. They don't reset or they don't trip when they should. I have changed more than a few out that were a burnt up mess when I pulled them out of the box. Not much troubleshooting involved in those.Top of the list, bad receptacles.
....