Re: GFCI compliance
Does the building need them? No. Should you install them anyway. My answer is "yes." Consider this:
A circuit breaker that supplies power to most of the stuff you will see in a break room or a restroom will be either 15 amp or 20 amp. Let's talk about the smaller one, the 15 amp breaker. Let's talk about the load that is normally on such a breaker. Let's say it is relatively heavily loaded: 12 amp load.
Now suppose that some device (microwave oven, toaster oven, coffee pot, hair dryer, whatever) has an internal breakdown. A person touching the device could get a shock. Because the body has much more resistance than, say, the coffee pot, there won't be much current flowing through the "victim." I will use that term for the following reason. A current of one tenth of an amp is enough to kill. But if you add that one tenth of an amp to the 12 amps already being drawn by the circuit, the total current will only be 12.1 amps. That will not cause the 15 amp breaker to trip.
Bottom line: 120 volts can kill, and the circuit breaker WILL NOT save you.
That is why GFCI circuits are worth the small cost of having them installed. They will trip on a current that is twenty times smaller than a potentially fatal shock.