E eagle Member Nov 19, 2003 #1 Need a clarification on this please. Sec. 210.11 calls for 20 OCD on the breaker feeding the protected bath/kitchen .... but do the actual GFCI devices need to be rated for 20 amp as well?
Need a clarification on this please. Sec. 210.11 calls for 20 OCD on the breaker feeding the protected bath/kitchen .... but do the actual GFCI devices need to be rated for 20 amp as well?
tonyi Senior Member Nov 19, 2003 #2 Re: GFCI Device ratings vs. sec. 210.11 A GFCI receptical could be either a 15 or a 20. The 15's are rated for 20A feedthrough
Re: GFCI Device ratings vs. sec. 210.11 A GFCI receptical could be either a 15 or a 20. The 15's are rated for 20A feedthrough
E eagle Member Nov 19, 2003 #3 Re: GFCI Device ratings vs. sec. 210.11 Thanks for the speedy response. Inspection in an hour