While I'd like an answer to the specific problem I encountered I'm looking more for theory as to what is happening than specifics.
Background:
Continuing on the helping the neighbor and hooking up their disposal I installed a GFCI after a switch. I removed all of the previous electrical romex (which was DUCT TAPED), installed 3/8 shielded to the outlet, grounded the outlet. Installed a switch, grounded said switch and box, and ran the armored cable back to the previously utilized junction.
The panel breaker was installed and labeled previously as only a disposal. I haven't traced the connection to verify it. I did have to splice and nut the armored to romex inside of the previously used junction box, and I did piggy the ground to the metal box as well.
Problem:
Immediately upon turning on the switch the GFCI flashes red once, and turns off. Resetting repeats the flash once, then off. The GFCI has no power, indicating a fault state. This is at the end of the circuit, with nothing attached to the outlet, and yet... the theory to me is that there is an imbalance between line and neutral- except there is nothing plugged into the outlet!
I then grabbed another GFCI (She had an old one), and it too indicated a fault state and wouldn't stay energized. I did not go back with a third GFCI (yet).
I plugged in a circuit tester to ensure that line/neutral weren't reversed somewhere else, and all three were good- ground, line, neutral.
What am I missing here? If there is something else on this line, how is it faulting the GFCI? The junction box I used to convert the armored back to romex (previously installed romex) has a ground onto the box itself- could something be powering the earth there, that's following the metallic sheath to the GFCI? Is it possible to have a DC Offset voltage mess things up?
I've already told her her panel looks atrocious- and recommended a master electrician I've worked with in the past. The panel is full of splits including a phase-jumped one to power the stove (taking up a single slot instead of 2...). I haven't pulled open the panel as I'm quite afraid to find there. But I am really not understanding what's happening with the GFCI and how it can go off at the end of a circuit if nothing is in it.
I appreciate your time for answering this probably very basic question.
Background:
Continuing on the helping the neighbor and hooking up their disposal I installed a GFCI after a switch. I removed all of the previous electrical romex (which was DUCT TAPED), installed 3/8 shielded to the outlet, grounded the outlet. Installed a switch, grounded said switch and box, and ran the armored cable back to the previously utilized junction.
The panel breaker was installed and labeled previously as only a disposal. I haven't traced the connection to verify it. I did have to splice and nut the armored to romex inside of the previously used junction box, and I did piggy the ground to the metal box as well.
Problem:
Immediately upon turning on the switch the GFCI flashes red once, and turns off. Resetting repeats the flash once, then off. The GFCI has no power, indicating a fault state. This is at the end of the circuit, with nothing attached to the outlet, and yet... the theory to me is that there is an imbalance between line and neutral- except there is nothing plugged into the outlet!
I then grabbed another GFCI (She had an old one), and it too indicated a fault state and wouldn't stay energized. I did not go back with a third GFCI (yet).
I plugged in a circuit tester to ensure that line/neutral weren't reversed somewhere else, and all three were good- ground, line, neutral.
What am I missing here? If there is something else on this line, how is it faulting the GFCI? The junction box I used to convert the armored back to romex (previously installed romex) has a ground onto the box itself- could something be powering the earth there, that's following the metallic sheath to the GFCI? Is it possible to have a DC Offset voltage mess things up?
I've already told her her panel looks atrocious- and recommended a master electrician I've worked with in the past. The panel is full of splits including a phase-jumped one to power the stove (taking up a single slot instead of 2...). I haven't pulled open the panel as I'm quite afraid to find there. But I am really not understanding what's happening with the GFCI and how it can go off at the end of a circuit if nothing is in it.
I appreciate your time for answering this probably very basic question.