fletcher
Member
- Location
- Detroit Michigan
So, if an ungrounded 3-prong plug can be down current of a GFCI plug and meet NEC....can you just put the whole circuit on a GFCI breaker in the panel?
480sparky said:As long as any grounds that are present are not hooked up. 406.3(D)(3)(c)
Dennis Alwon said:Hold on there-- If the first half of the circuit has an EG and the second half does not then you can keep the EG connected to the first half.. Not sure why anyone would do that other than no room in the box but i wanted to be clear.
Once you get to the ungrounded section than you cannot hook up any EGC that is not connected thru to a panel. The ones that have no EGC must be marked.
480sparky said:I read the last sentence of 406.3(D)(3)(c) as saying you do not hook up any grounds.
Dennis Alwon said:I believe that is saying if one installs the 3 wire receptacles where there is no EGC then you cannot run an EGC between the receptacles. THis is to make sure someone later does not think there is a ground. IMO.
480sparky said:So suppose the first half of the circuit is ungrounded, and the second half has a ground present, but is not grounded?
I would think that is a better possibility than the first half with a ground, but further down does not.
Dennis Alwon said:Then I agree you cannot hook up the grounds and they must be marked. I have seen both situation. New circuit that ties to an old circuit and new wiring added to an old non grounded circuit.
Why would you not want to connect the EGC if it is a legitimate one. Obviously we do it all the time when an new circuit feeds a room then continues on to pick up an old circuit. If the GFCI is present at the panel then those receptacles that have valid EGC would get connected and those downstream would not.
Maybe I am misunderstanding-- I apologize if that is the case.
480sparky said:I guess you could hook up the ground, if it is indeed grounded. But I've never seen a situation where someone extended a grounded circuit with an ungounded wiring method.