I see that 680.21C in 2014 requires GFCI protection for pool pump motors. I have a residential home inspector requiring a GFCI be installed on a pool pump that was installed in 2001. Wouldnt that be grandfathered.
 
I see that 680.21C in 2014 requires GFCI protection for pool pump motors. I have a residential home inspector requiring a GFCI be installed on a pool pump that was installed in 2001. Wouldnt that be grandfathered.

A home inspector can't require anything. Explain to the customer that he is incorrect, give them the option of updating the connection if they want to go to the expense.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I see that 680.21C in 2014 requires GFCI protection for pool pump motors. I have a residential home inspector requiring a GFCI be installed on a pool pump that was installed in 2001. Wouldnt that be grandfathered.


Many home inspectors make recommendations like that however it is a negotiation that the buyer and seller can work out. They often recommend gfci in kitchens that are old. Again if the seller wants to oblige then we do it otherwise it is not done
 

macmikeman

Senior Member
This year 5 or six times I have charged $700-800 for replacing 4 or 5 kitchen outlets to gfi ones thanks to a HI stressing the need to convert in his home report to property buyers. In and out in under an hour. I just loves me some home inspectors......
 

JFletcher

Senior Member
Location
Williamsburg, VA
I see that 680.21C in 2014 requires GFCI protection for pool pump motors. I have a residential home inspector requiring a GFCI be installed on a pool pump that was installed in 2001. Wouldnt that be grandfathered.

It is 680.22 (B) in the 2008 NEC. I found this thread:


http://forums.mikeholt.com/showthread.php?t=109667

which seems to indicate GFCI were required on pool pump motors back in 1999. If it did require a GFCI when it was built and lacks one now, no, it wouldnt be grandfathered in.

As others have written the HI cant require anything.
 

iwire

Moderator
Staff member
Location
Massachusetts
A home inspector can't require anything. Explain to the customer that he is incorrect, give them the option of updating the connection if they want to go to the expense.

Hold on, I am willing to get the home inspector did not say to anyone a GFCI is required to be installed. They recommended it and now that is part of the sakes negotiations.
 

iwire

Moderator
Staff member
Location
Massachusetts
This year 5 or six times I have charged $700-800 for replacing 4 or 5 kitchen outlets to gfi ones thanks to a HI stressing the need to convert in his home report to property buyers. In and out in under an hour. I just loves me some home inspectors......

Good for you, make some money. So many electricians seem to feel the need to prove the HI wrong, like it is some sort of competition.
 