A/A Fuel GTX
Senior Member
- Location
- WI & AZ
- Occupation
- Electrician
I have a situation in a parking lot of a government facility that utilizes cord connected engine block heaters to its vehicles that remain outside. They are currently on GFCI receptacles as per 210.8 (B) (4).Extension cords are commonly used to reach the vehicles. The problem is that we are experiencing a lot of tripped receptacles during the overnight hours and come morning, the engines don't like to start because of the extreme cold. Now, the wording in 210.8 (B) (4) states accessible to the public as part of the requirement. Are employees considered the public or could we remove the GFCI protection and eliminate the nuisance trips? The vehicles are in a secure, fenced in area. Any thoughts?