Is there any NEC requirement for GFCI for hard wired permanently mounted equipment

lkjhoftygiujok;lmcnjvbhfgsurhwiljoefk;ladsmnjbdvhguhiljfo;kwldANBJCVHGIJFLKWDknjhfkw
xjkjbhhjkjhgyftyguhijoklcknbjmhv gukhiljknbjcmvhguhiljknbjmhvguhkilhughbjhikjhbckhjkbscs
 
Care to elaborate what kinda equipment? 210.8(C) and (D) come to mind, article 680 also comes to mind.
 
If there is an "outlet" involved (as opposed to a receptacle) 210.8(C),)(D) & (E)
and, as mentioned, Art 680
and Art 422.5
 
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
 
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
No requirement for a water heater to be GFCI protected.
They do need to be grounded, but not GFCI protected.
 
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
The minimum character requirement is for a new thread only. Any post after the OP doesn't require a minimum. Also, I believe the minimum is 100 characters.