Is there any NEC requirement for GFCI for hard wired permanently mounted equipment

lkjhoftygiujok;lmcnjvbhfgsurhwiljoefk;ladsmnjbdvhguhiljfo;kwldANBJCVHGIJFLKWDknjhfkw
xjkjbhhjkjhgyftyguhijoklcknbjmhv gukhiljknbjcmvhguhiljknbjmhvguhkilhughbjhikjhbckhjkbscs
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Care to elaborate what kinda equipment? 210.8(C) and (D) come to mind, article 680 also comes to mind.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If there is an "outlet" involved (as opposed to a receptacle) 210.8(C),)(D) & (E)
and, as mentioned, Art 680
and Art 422.5
 

wireday

Senior Member
Location
New England
Occupation
Master electrician
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
No requirement for a water heater to be GFCI protected.
They do need to be grounded, but not GFCI protected.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
the equipment is a large water heater, hard wired no receptacle, for some reason every now and then the site makes me have 200 characters
The minimum character requirement is for a new thread only. Any post after the OP doesn't require a minimum. Also, I believe the minimum is 100 characters.