GFCI for Pentair VS pool pumps

74sparks

Member
Location
Pennsylvania
Occupation
Electrical Engineer
I think most are aware by now that the Pentair VS pool pumps don't play well with many brands of GFCI breaker. But short of swapping the whole panel out for Siemens, what solutions exist for adding GFCI to a type-CH panel, when upgrading to a Pentair VS pump? A type-CH 220 GFCI breaker has already been tested here, and experienced random trips.
 
Figured that was going to be the path. Is any particular Siemens series favored for VS/VFD motors, or do they all play equally well?

I've seen Pentair PA220GF breakers around, mostly at pool and spa suppliers. But short of their IntelliCenter automation load centers, I don't think I've ever seen a simple 2-space load center from Pentair. :unsure:
 
Figured that was going to be the path. Is any particular Siemens series favored for VS/VFD motors, or do they all play equally well?

I've seen Pentair PA220GF breakers around, mostly at pool and spa suppliers. But short of their IntelliCenter automation load centers, I don't think I've ever seen a simple 2-space load center from Pentair. :unsure:
No idea if one Siemens series is better than another for this application. I think the Pentair breaker is a rebranded Seimens, but not sure
 
I always thought they looked similar, but hadn't noticed how much, until you said that. I'd say we have a visual match... PA220GF for QF220A.

PA220GF:
1720736398723.png

QF220A:
1720736431898.png
At least that gives me a load center to shop.

Thanks!
 
Our project has a spa with one main circulation pump and two jet pumps. We will have more pumps once the pool is designed. Our Pentair Intellicenter control panel is only for controls as we will have too many pieces of equipment to control to also have the two pole GFCI breakers for the pumps in it. Our feeders for the boilers, the pumps on the hydronic snow melt system, the spa pumps, site power and lighting are in a Siemens P1 panel. This panel has bolt-on type BL breakers, not the little type QP plug-in breakers. So we cannot use the "recommended" Pentair PGF breaker, PA220GF.
I contacted both Pentair and Siemens about this issue. Pentair told me that I needed to use a 6mA GFCI breaker or I would have continued tripping! ALL Class A GFCI breakers have a 5mA +-1mA trip rating (per UL 943). So obviously we're using a Class A GFCI breaker. They no longer manufacture Class B GFCIs and a Class C is for equipment protection ONLY! Pentair also told me that we may have a neutral issue, after I told him we had two-pole GFCIs and the motors were wired up 208 singl-phase two wire. WE HAVE NO NEUTRAL!
Siemens called me back to respond to my email. They told me that "Yes, we do not make a specific 6mA rated GFCI breaker". I was also told that Pentair sends people to Siemens to physically go through and test breakers to see where their break open / tripping point is. They would buy the breakers that would trip on the higher end of 6mA. These Siemens breakers are then relabled with Pentairs own label! I asked him to email me this statement but have not yet gotten anything back. Pentair only does this with the Type QP single-pole and double-pole 20A GFCI breakers, so we are SOL to try and get a bolt-on Pentair branded, 50% markup price GFCI breaker.
This to me sounds more like the Pentair labeled breaker is required than it is "recommended"! Which if that is the case, can that be legal? They make motors that you HAVE to buy their breaker, not any other brand.
To me it sounds like Pentair has an issue with their VFDs creating too much noise, causing the breakers to trip. Maybe Pentair needs to finally fix THEIR issue of the motors tripping the GFCIs.
After doing approximately 16,000,000 hours of research on Pentair IntellifloXF VSF and Whisperflo VST tripping Siemens 2-pole GFCI breakers. I finally (hopefully) found an answer.
Supposedly (not supposebly), back in August of 2023, member ddbear installed a ferrite toroid core FT240-43. Post 2854953. His last post was two months later. He stated that after two months he had ZERO trips!
Has anyone else tried this?
Moderator Jraef was also part of this conversation.
I don't know if there is a way to contact someone directly to find out if ddbear sitll has a zero trip Pentair pump?
If this ferrite core is the secret to an unknow number of GFCI tripping nightmares, Pentair could, and should, simply supply their motors with ferrite cores!! Or have their enginneers fix their own known issue that has been around for over a decade!! My other fix is that no one ever buy Penair products again.
 
I can understand your frustration. I don't use Pentair controls, only Jandy, and I am aware of the Pentair breaker and the tripping issues.

I have a client, homeowner, I have been consulting for that has 3-year-old pool. Original builder screwed up and I was called.

All the equipment is Pentair including the control system. I added an additional Pentair pump and added the Pentair upgrade control system as there was no remote operation. I purposely purchased the Pentair 2 pole PA 220GF for this pump. I did not want to risk any tripping issues.

The Pentair rep I know tells me the proprietary breakers will be going away, and they are working on a fix. When, I don't know.

Any of my projects where the 100-amp Jandy sub exceeded the number of spaces for devices to be used, a separate panel was used. Any off the shelf breaker could be used. Easy peasy. Jandy has multiple power center choices so you can have up to 32 auxiliaries. I've never had any tripping issues with Jandy.

I guess your choices are getting the ferrite toroid cores and hope they work or tear out the Pentair system and replace with a Jandy.
 