2008 NEC......680.22(B)......Does the new wording really require the hard-wired pool pump to be ground fault protected?
volt102 said:2008 NEC......680.22(B)......Does the new wording really require the hard-wired pool pump to be ground fault protected?
This change reinstates the 1999 code language requiring GFCI protection on single-phase hard wired pump motors to ensure safety for swimming pool users.
mdshunk said:For me and mine, I GFCI every pool pump anyhow. Just seems like the right thing to do, to me. Pool equipment is often very neglected during its life unless it just plain up and totally quits.
iwire said:IMO yes or is there more to your question then I am realizing?
volt102 said:It states this requirement is to be applied to direct-connected pumps only when those outlets are supplied from short-circuit and ground-fault protected circuits to be GFCI protected.
Had some electricians arguing until I caught one side interchanging the terms 'ground-fault protected' with 'ground-fault circuit-interrupter'.
Definitions, Definitions, Definitions!
I also always gfci protected them in the past.