I made a "better safe than sorry" decision to gfi the receptacle inside a walk-in freezer.
It feeds the heat tape for the condensate line. The circuit also feeds the door heating elements and the inside light.
I got a call back that the gfci was tripping and wouldn't reset. When I got there I worked my way through the circuit item by item because the hot wire off the load side of the gfci was ohm'ing out to ground.
I finally figured out that one of the door heating elements was the culprit (it had 2 different elements)
When I reported back to the maintenance guy about the issue I initially just said "element is bad". He started to get critical that I had it on a gfci and had some reason why GFCI's aren't good with those heating elements. He said they had several that weren't gfci'd and worked fine. I told him I couldn't imagine installing a receptacle in that environment and not gfci'ing it!
When I explained that it ohm'd out to ground he totally changed his tune!
My question is, looking at the code trying to find a reference that applies to my install the main item I see is 210.8(B)(6) Indoor wet locations.
Is there anything more specific that I'm not seeing that applies to the inside of a walk-in freezer?
It feeds the heat tape for the condensate line. The circuit also feeds the door heating elements and the inside light.
I got a call back that the gfci was tripping and wouldn't reset. When I got there I worked my way through the circuit item by item because the hot wire off the load side of the gfci was ohm'ing out to ground.
I finally figured out that one of the door heating elements was the culprit (it had 2 different elements)
When I reported back to the maintenance guy about the issue I initially just said "element is bad". He started to get critical that I had it on a gfci and had some reason why GFCI's aren't good with those heating elements. He said they had several that weren't gfci'd and worked fine. I told him I couldn't imagine installing a receptacle in that environment and not gfci'ing it!
When I explained that it ohm'd out to ground he totally changed his tune!
My question is, looking at the code trying to find a reference that applies to my install the main item I see is 210.8(B)(6) Indoor wet locations.
Is there anything more specific that I'm not seeing that applies to the inside of a walk-in freezer?