gmayeux

Member
When installing a small tankless water heater under pedstal type lavatory is ground fault protection required by code. the tankless is 230 volt cord and plug connected.
 
gmayeux said:
When installing a small tankless water heater under pedstal type lavatory is ground fault protection required by code. the tankless is 230 volt cord and plug connected.

No, see 210.8
 
gmayeux said:
When installing a small tankless water heater under pedstal type lavatory is ground fault protection required by code. the tankless is 230 volt cord and plug connected.

I don't see anything in Article 422 either.
 
Pierre C Belarge said:
Do not forget to check the installation instructions, there may or may not be provisions for GFCI protection located there.
I've managed to spot a GFCI requirement in the instructions for most of the whole-house type on-demand water heaters, such as Rinnai. The point of use one's, like eEmax, don't seem to have that requirement.
 
mdshunk said:
I've managed to spot a GFCI requirement in the instructions for most of the whole-house type on-demand water heaters, such as Rinnai. The point of use one's, like eEmax, don't seem to have that requirement.
The ones that require 50 plus amp, 240 volt circuits?
 
don_resqcapt19 said:
The ones that require 50 plus amp, 240 volt circuits?
No, natural gas or propane, such as the Rinnai one I used as an example. They typically take a 120 volt circuit that draws something like .7 of an amp.

Takagi, Noritz and Bosch are three other common brands
 