I installed a 2 pole 50 amp GFCI breaker for a hot tub group. The display read error. I had the proper voltage at the tub. The hot tub people said since its a three wire hookup, the ground goes on the ground bar in the panel not in the neutral lug of the breaker. I changed it and the tub works. Is that breaker still protecting from shock?
 
A gfci will work without the neutral connected if the tub does not require a neutral but the white wire from the breaker must be terminated on the neutral bar
 
A gfci will work without the neutral connected if the tub does not require a neutral but the white wire from the breaker must be terminated on the neutral bar
Makes sense. With no neutral in the branch circuit, the GFCI breaker is measuring the difference between the L1 and L2 as opposed to L1, L2, and N... but if that's the case, why does the breaker neutral pig tail still need to go to the neutral bus if there's no control circuit current being pulled?

Side bar: What hot tub would NOT have a control circuit? Is there even such a thing?
 
I installed a 2 pole 50 amp GFCI breaker for a hot tub group. The display read error. I had the proper voltage at the tub. The hot tub people said since its a three wire hookup, the ground goes on the ground bar in the panel not in the neutral lug of the breaker. I changed it and the tub works. Is that breaker still protecting from shock?
As far as I'm aware, the GFCI breaker itself is NOT utilizing the ground / wire-type EGC in protection of the circuit. The wire type EGC is there to clear the fault. The GFCI breaker itself is measuring the current on L1, L2, and N (if you have it) for protection.

1601938027765.png
 
Makes sense. With no neutral in the branch circuit, the GFCI breaker is measuring the difference between the L1 and L2 as opposed to L1, L2, and N... but if that's the case, why does the breaker neutral pig tail still need to go to the neutral bus if there's no control circuit current being pulled?

Side bar: What hot tub would NOT have a control circuit? Is there even such a thing?


The neutral is needed for the electronics inside the gfci.

Yes there are many tubs that are straight 240V. Transformers can do lots of things...LOL
 
As far as I'm aware, the GFCI breaker does NOT utilize the ground / wire-type EGC in protection of the circuit. The wire type EGC is there to clear the fault. The GFCI breaker itself is measuring the current on L1, L2, and N (if you have it) for protection.

View attachment 2553836


That is correct. That is why a gfci works even when a receptacle does not have an equipment grounding conductor.
 
Is that breaker still protecting from shock?
Do you know "the thumb rule" for determining the direction of the magnetic flux? It should help you understand how this breaker is still providing protection.
 