Hello all.
I am bidding a small job for a local dentist. Replacing a non compliant feed to the existing vacuum pump, fed with NM, and installing a second feed for the new pump as it needs two feeds.
240 volt, single phase. 20 amp. It seems to me that these feeds should be GFCI protected given they handle the waste water from the dental operations. Manufacturer instructions state that local AHJ should determine GFCI, NEC guidelines should be followed, etc. I have heard a lot of people say "hardwiring equipment negates the GFCI requirement,"ART 422 seems to indicate otherwise. On another note that does not apply in this case, I also hear people say a monoplex or some call them simplex receptacle, i.e. the single point of use style receptacle negates GFCI in some instances. I don't see where this is justified in the code either. Please feel free to expound if you feel compelled.
At any rate, it would seem that while this pump is hardwired, voltage to ground is less than 150, less than 60 amps, GFCI should still be placed in the panel of the breaker type because it handles water ?
I spend a lot of time in my own head....2nd, 3rd, 4th guessing my decisions. Please tell me your thoughts.
Thank you all in advance.
I am bidding a small job for a local dentist. Replacing a non compliant feed to the existing vacuum pump, fed with NM, and installing a second feed for the new pump as it needs two feeds.
240 volt, single phase. 20 amp. It seems to me that these feeds should be GFCI protected given they handle the waste water from the dental operations. Manufacturer instructions state that local AHJ should determine GFCI, NEC guidelines should be followed, etc. I have heard a lot of people say "hardwiring equipment negates the GFCI requirement,"ART 422 seems to indicate otherwise. On another note that does not apply in this case, I also hear people say a monoplex or some call them simplex receptacle, i.e. the single point of use style receptacle negates GFCI in some instances. I don't see where this is justified in the code either. Please feel free to expound if you feel compelled.
At any rate, it would seem that while this pump is hardwired, voltage to ground is less than 150, less than 60 amps, GFCI should still be placed in the panel of the breaker type because it handles water ?
I spend a lot of time in my own head....2nd, 3rd, 4th guessing my decisions. Please tell me your thoughts.
Thank you all in advance.