If there is an outlet in a master bedroom that is within 6 feet of a shower in the master bathroom when the bathroom door is open does that outlet need to be GFCI protected?
I thought going through a door didn't count in the requirement?
The doorway has been removed in the 2020 edition. This will change things such as a recep under sink as the cabinet door is no longer a barrier.I thought going through a door didn't count in the requirement?
The doorway has been removed in the 2017 edition. This will change things such as a recep under sink as the cabinet door is no longer a barrier.
The shower requirement isn't even in the 2014, so how can it have been taken out in 2017?
I had a typo. I meant 2020. I fixed it.
210.8. In 2017 a door was considered a barrier. For 2020 a door is no longer a barrier.So where is the door reference to begin with?
Does that mean if a receptacle is 1 foot away from a door, the first one on the other side of the wall can be 11 feet away?210.8. In 2017 a door was considered a barrier. For 2020 a door is no longer a barrier.
I don't think he was referencing the spacing for general receptacles. I think he was referencing the rules for measuring whether a GFCI would be required. Used to be doing through a door didn't count in the measurement. I think it said something along the lines of .............measurements are the distance without doing through doorways, bla, bla, .........Does that mean if a receptacle is 1 foot away from a door, the first one on the other side of the wall can be 11 feet away?
I'm not talking about spacing.Does that mean if a receptacle is 1 foot away from a door, the first one on the other side of the wall can be 11 feet away?
How would you measure for this rule with an imaginary circle centered on the sink that must also encompass the door?However in the 2020 code, if that receptacle is within 6' of the bathroom sink, GFCI protection will be required.
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit interrupter shall be installed in a readily accessible location.
Informational Note No. 1: See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
Informational Note No. 2: See 422.5(A) for GFCI requirements for appliances.
Informational Note No. 3: See 555.9 for GFCI requirements for boat hoists.
Informational Note No. 4: Additional GFCI requirements for specific circuits and equipment are contained in Chapters 4, 5, and 6.
For the purposes of this section, when determining the distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a window.
For the purposes of this section, when determining distance
from receptacles the distance shall be measured as the shortest
path the cord of an appliance connected to the receptacle
would follow without piercing a floor, wall, ceiling, or fixed
barrier, or passing through a door, doorway, or window
IMHO - This section was changed due to "Ifs" What if the bath flooded and some one plugged a wet vac into the bed room outlet. Then what if it had a tattered cord and a child stepped on it with the wet floor. Or what if some one was giving the dog a bath then tried to blow dry him with the bed outlet. If the St Bernard whilst dripping wet licked the dryer that had a fault in it.