Gfci in lab

Status
Not open for further replies.

jcole

Senior Member
Hello guys and gals.

I noticed in our industrial lab that the countertop receptacles used for testing equipment was not gfci protected and are within 6' of a sink. I am assuming they did not need to be back in the late eighties when the building was built.

Are they required now? If so, when did that change?

My code book is at work and it is the 2008 code.

Thanks for the replies.
 
Hello guys and gals.

I noticed in our industrial lab that the countertop receptacles used for testing equipment was not gfci protected and are within 6' of a sink. I am assuming they did not need to be back in the late eighties when the building was built.

Are they required now? If so, when did that change?

My code book is at work and it is the 2008 code.

Thanks for the replies.

There is an exception for this in 210.8(B)(5) in the 2017 NEC. As I recall, this exception has been in the code since about the 2008 edition.
 
so sump pumps were disallowed since 2005 iteration?

but the sump specs call for the gfi anyway
 
so sump pumps were disallowed since 2005 iteration?

but the sump specs call for the gfi anyway

It looks like sump pumps were excepted from the requirement since 1990. Installation instructions can be more stringent.
 
To answer the op questions perhaps this is the case
(5) Sinks — where receptacles are installed within 1.8 m
(6 ft) of the outside edge of the sink
Exception No. 1 to (5): In industrial laboratories, receptacles
used to supply equipment where removal of power
would introduce a greater hazard shall be permitted to be
installed without GFCI protection.
 
If GFCI wasn't required at the time of installation they are still code compliant if unchanged. That don't mean OSHA or an insurance company won't want it changed anyhow.

Sump pumps do not require GFCI protection. If they are cord and plug connected the receptacle outlet may still require GFCI protection though, this is dependent on outlet location and not what the load is.
 
If GFCI wasn't required at the time of installation they are still code compliant if unchanged. That don't mean OSHA or an insurance company won't want it changed anyhow.

Sump pumps do not require GFCI protection. If they are cord and plug connected the receptacle outlet may still require GFCI protection though, this is dependent on outlet location and not what the load is.

• Risk of electric shock. This pump is supplied with a grounding conductor and
grounding-type attachment plug. Install or connect to a circuit that is protected by a
GFCI, ground fault circuit interruptor.

From https://s3.amazonaws.com/pumpproduc...11+Sump-Effluent+Pump+Installation+Manual.pdf

But I digress.
 
It looks like sump pumps were excepted from the requirement since 1990. Installation instructions can be more stringent.
excepted from what requirement? Sump pumps were never directly required to have GFCI protection by NEC. They often get plugged into receptacles that are in a location that requires protection though. There used to be an exception for single receptacles for dedicated appliances to be omitted from GFCI protection requirements, but that went away in either 2002 or 2005 I believe (I'm leaning more toward 2005).
 
excepted from what requirement? Sump pumps were never directly required to have GFCI protection by NEC. They often get plugged into receptacles that are in a location that requires protection though. There used to be an exception for single receptacles for dedicated appliances to be omitted from GFCI protection requirements, but that went away in either 2002 or 2005 I believe (I'm leaning more toward 2005).

2008 IIRC.
 
It is worth noting that the exception has its limitations:
Exception No. 1 to (5): In industrial laboratories, receptacles used to supply equipment where removal of power would introduce a greater hazard shall be permitted to be installed without GFCI protection.
That does not mean that receptacles in labs don't need GFCI protection. You have to consider what will be plugged into the receptacle, and what bad thing might happen if that item loses power. If a GFCI trips and ruins a lab experiment so that they will have to start it all over again, that is not a sufficient reason for removing the GFCI device from the circuit. If on the other hand some type of chemical mixing is going on, and if a loss of power would cause the release of toxic fumes into the room, then it is appropriate not to have GFCI protection for that circuit.
 
data dialer for phase loss monitor

data dialer for phase loss monitor

2008 IIRC.

I still think that sump pumps and freezers with dedicated receptacles should have only been installed before 2008.
Also garage door outlets on the ceiling

one workaround is to get a battery backup on the power and connect it to a dialer that will let you know when the power went out.
We used to have alot of that at work, but that was with POTS.
I wonder how we would do that now with a data line?
 
I still think that sump pumps and freezers with dedicated receptacles should have only been installed before 2008.
Also garage door outlets on the ceiling

one workaround is to get a battery backup on the power and connect it to a dialer that will let you know when the power went out.
We used to have alot of that at work, but that was with POTS.
I wonder how we would do that now with a data line?

Don't know what is all out there, but probably is applications and services that can notify you via data line. I also imagine you still can connect a traditional "dialer" to some VOIP type devices.
 