rick hart
Senior Member
- Location
- Dallas Texas
Can someone tell me what an Industrial Laboratory is? Would a large medical research or pathpology lab be considered "industrial" by the CMP?
Thanks
Thanks
Thanks for pointing that out, Tom. I keep looking first at the 2005 edition, and did not notice that one.. . . there is an exception for "industrial laboratories" GFCI protection in 08 NEC 210.8 B 5
Maybe they meant lavatory :grin:Can someone tell me what an Industrial Laboratory is? Would a large medical research or pathpology lab be considered "industrial" by the CMP?
Thanks
It?s not the sink that causes the hazard. It?s an item plugged into a receptacle that could cause a hazard if it lost power. One example might be a chemical or biological experiment for which a loss of power to a pump or a fan or a mixer or something might lead to a release of nasty stuff into the lab environment. Not a likely scenario, but the only one I can come up with for now.I can't figure out where any industrial sink would cause a greater hazard but that really isn't the question after all.
Now I am lost. New lab, but old building, and not a result of a recent renovation? If a new Principal Investigator moves in to an old building, and is willing to work with the existing power, water, and gas services, and if you therefore do not need to do any renovations, then the NEC is not a player in the arrangements. You can upgrade the wiring, even if the NEC does not require it, if the owner (or the PI) is willing to pay the costs. But you don?t have to.My question is based on what to do with a fairly new lab in use now. Safety folks look at the current code and say the installation is outside of code- true enough. When the Lab was built- under 93 NEC- no problem.
Again, I don?t understand. What is the matter with plugmold? Are you saying there is no GFCI receptacles installed along this raceway? Feel free to put one in, if you like. It shouldn?t require pulling or replacing any wiring, unless you are telling us that the present receptacles are not even grounded.The specific problem is in places where plugmold was used to provide outlets across the lab workbench and sinks and to complicate matters- shared neutrals were used in multi-circuit configuration.
You stop when the dollars stop. It?s as simple as that. The NEC is all about a minimum standard of safety, not about absolute safety and the elimination of any possibility of any injury ever.But, where do you stop with the NEC after the fact in keeping folks safe enough?
Probably not. Why should it?Parts of the hospital were wired with AL THW in the 60's; does that need to come out too? Probably.
I can't figure out where any industrial sink would cause a greater hazard but that really isn't the question after all:
My question is based on what to do with a fairly new lab in use now. Safety folks look at the current code and say the installation is outside of code- true enough. When the Lab was built- under 93 NEC- no problem.
The specfic problem is in places where plugmold was used to provide outlets across the lab workbench and sinks and to complicate matters- shared neutrals were used in multi-circuit configuration.
So, its not that I have a problem with the GFCI protection, I have a problem pulling out and chunking several hundred feet of hospital grade plugstrip to comply with the current code. Unless the area undergoes renovation, of course. I'm good with that.
I know NEC does not apply after the fact, assuming the area met code at the time of installation. But,where do you stop with the NEC after the fact in keeping folks safe enough? Parts of the hospital were wired with AL THW in the 60's; does that need to come out too? Probably. In the grand scheme of things in a 80 year old facility, there are bigger fish to fry (no pun intended) if bringing a facility up to current code every three years is the goal. I'm starting to whine...
Thanks