What is the distance from a sink located on an island and also on a countertop that a GFCI inside a lab needs to be located? Is it supposed to be 6 ft? What article refers to this?
 

charlie

Senior Member
Location
Indianapolis
Re: GFCI in laboratory

If this is not a bathroom, rooftop, or a kitchen, 210.8(B) does not require one. Of course there are other locations like farmsteads, commercial garages, health care facilities, etc. but your laboratory doesn't appear to be one of those.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: GFCI in laboratory

We've seen a lot of these type questions. I always wonder:
Does someone not want a GFCI? Perhaps due to cost.
Or do they want a GFCI? For safety.

Remember the NEC is a minium. And with the new UL 2003 GFCI standard, GFCI prices will probably double. Stock up now.
 

solomomj

Member
Location
Texas
Re: GFCI in laboratory

The question was posed for safety. I believe that a GFCI should be installed, but powers above me seem to not be able to use "common sense" about electrical/safety requirements?! I was hoping to get proof, so I could avoid trying to use logic on our so intelligent management!!!! :D
 