210.8 Ground-Fault Circuit-Interrupter
Protection for Personnel
Ground-fault circuit-interruption for personnel shall be pro-
vided as required in 210.8(A) through (C). The ground-fault
circuit-interrupter shall be installed in a readily accessible location.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
210.8(A)(1) through (8) shall have ground-fault circuit-
interrupter protection for personnel.
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas, and
areas of similar use