GFCI labeling

Status
Not open for further replies.

bcgill

Member
Location
New Mexico
406.3(D)(3)(c) Requires these receptacles to be marked "GFCI Protected". Is there a code requirement for other GFCI receptacles to be marked?

Bob
 

hurk27

Senior Member
Re: GFCI labeling

This is the only place I could find. which is about the tech power supply 60/120 volt system

647.7 Receptacles.
(2) All outlet strips, adapters, receptacle covers, and faceplates shall be marked with the following words or equivalent:
WARNING ? TECHNICAL POWER
Do not connect to lighting equipment.
For electronic equipment use only.
60/120 V. 1ac
GFCI protected
 

bphgravity

Senior Member
Location
Florida
Re: GFCI labeling

I do not believe it is an actual code requirement however, regular receptacles that are GFCI protected should be labeled identifying this. This is why GFI's come with the little "GFI protected" stickers.
 
A

a.wayne3@verizon.net

Guest
Re: GFCI labeling

The new leviton gfci`s come with english and spanish stickers now we can protect all languages
 