Re: GFCI Nusance Tripping?
I agree with iaspiretowire. You are fine, and his ex-boss was wrong.
Current leaves the ?hot pin? of one receptacle, enters the 5 amp drill at the hot half of its plug, goes through the drill, returns to the neutral half of the plug, enters the neutral pin of the receptacle, and only then joins with any other current flowing through the shared neutral. Current leaves the ?hot pin? of the other receptacle, enters the 10 amp saw at the hot half of its plug, goes through the saw, returns to the neutral half of the plug, enters the neutral pin of the receptacle, and only then joins with any other current flowing through the shared neutral. Each of the two GFCI receptacles will see only the current flowing out of it and returning to it. So long as each GFCI sees the same current on each of its two legs, neither will trip. The existence of the shared neutral does not enter into the comparison that each GFCI receptacle makes between its hot current and its neutral current.