GFCI on an _ungrounded_ system

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
In another thread, the comment was made that a GFCI would not work on an ungrounded system.

Rather than respond in an already confused thread, I decided to move that discussion into a new thread.

IMHO a GFCI would function to reduce the severity of shocks if installed on an ungrounded system. The basic method that a GFCI uses, detecting any net current flow on the sensed conductors, will work just fine from any supply suitable to power the GFCI electronics.

Where the function will be different is that the characteristics of any ground fault will be different on an ungrounded system, and this will change the response of the GFCI.

In an idealized 'ungrounded' system, a single ground fault will cause _no_ current to flow. On such a system, a GFCI would not detect such a ground fault, because no current was flowing through it. Of course, on such a system, such a ground fault would not cause a shock! You can't get shocked by having zero current flow though your body.

In the real world, there is no such thing as an ungrounded system. The closest that we get is a system that is not intentionally grounded, but which is still 'capacitively' grounded. Because of this capacitive grounding, a ground fault will complete a circuit, and some current will flow through it. The magnitude of this current flow depends upon the total size of the system.

For industrial 'impedance grounded' 480V systems, the 'capacitive charging current' can be several amps. I imagine that a 'residential' ungrounded system (not that the NEC permits this) consisting of a small 120/240V transformer, non-metallic wiring methods, etc. would have a very small capacitive charging current.

If the capacitive charging current of the system is low enough, then ground fault current could never be high enough to trip a GFCI. The worst case could be if the ground fault current was as high as it could be without tripping the GFCI. A 4mA _continuous_ shock would not be enough to trip a GFCI, but might be quite uncomfortable. Of course, if the capacitive charging current is low enough, than not only would the GFCI not trip, but the shock would not even be perceived.

-Jon
 
Members just a heads up. Please stay directly on topic. If you have a related topic feel free to start another thread. Threads don't cost much, use as many as you want. :smile:
 
080914-1249 EST

winnie:

Anything that will cause an unbalanced current between the two wires thru the GFCI that is greater than about 5 MA will cause it to trip. Assuming as you said that there is enough power available to operate the GFCI.

120 V at 60 Hz and about 0.1 mfd (100,000 pfd) will provide approximately 5 MA.
Also leakage resistance of 24,000 ohms at 120 will produce 5 MA.

.
 
I understand, I guess I'm just like more visuals of the device in question.

The GFCI in Action.

gfci_circuit.gif


gfci_circuit_faulting.gif


My only problem with these diagrams is the placement of the Amperage labeling and would have moved everything closer to chasis.

These images were found using Goolge Image Search

http://images.google.com/images?hl=en&q=GFCI&btnG=Search+Images&gbv=2
&
http://images.google.com/images?gbv=2&hl=en&q=+site:www.rhtubs.com+GFCI

Note there are many others and two pole diagrams of Siemens and Square D ...

I just re-read the OP's title, I guess I goofed up, I got a EGC, Sorry winnie ...
The concept is still there but the fault is on a service ground also breaking from the Thread Theme...
I can't win, But I still get....
 
Last edited:
GFCI devices only look for residual current, they do not care if the fault current is flowing to ground or on some other conductive surface.

The only reason a ground (dirt) connection is required is if we want the GFCI to function on a fault path that includes earth. Because the NEC requires most our electrical systems to be bonded to dirt (ground), our GFCIs will protect us during ground faults. There are very few faults to ground(dirt), relative to faults to other possible conductive surfaces. Kitchen counters have many more issues with poorly/improperly bonded appliances than they do with fault paths that include a ground rod.
 