The information.i have gleaned from a manufactures electrical engineering dept say the only state requiring gfci on heat pumps is florida..and if the install has a permit the journeyman who install these pumps get an inspection passed with a gfci in the panel.inspectpr goes away and so does the gfci .they put a properly sized standard breaker based on mca and that stops the nuisance tripping associated with heat pumps.
Long story but I have aninstall on 2 large pumps 20k btu.47mca.a 50 would work but a 60 gives us roomier starting even tho these are inverter type pumps that soft start.got some wannabe interference from some of the board members of the organization that insist on gfci . Im gonna use some 30 mil tripping 60 amp gfcis because they insist. Only 250$ each.lol instead of 20 bucks.imho this is stupid is as stupid does. Bit the customer is always right eh?? Lol just don't call.me for this unattended load from 95 miles away if and when it trips.lol
away.lol
Long story but I have aninstall on 2 large pumps 20k btu.47mca.a 50 would work but a 60 gives us roomier starting even tho these are inverter type pumps that soft start.got some wannabe interference from some of the board members of the organization that insist on gfci . Im gonna use some 30 mil tripping 60 amp gfcis because they insist. Only 250$ each.lol instead of 20 bucks.imho this is stupid is as stupid does. Bit the customer is always right eh?? Lol just don't call.me for this unattended load from 95 miles away if and when it trips.lol