Strombea
Senior Member
- Location
- Prescott, Arizona, USA
I know that this has been discussed before, but i am having trouble on a service call. The run from panel is 100 ft, and it is a 3 wire circuit supplying 2 different GFCIs and nothing else. (outdoor kitchen) So the GFCI 1 goes out every 2 or 3 months and GFCI 2 seams to be fine. I know that GFCIs can share a neutral, personally i would have ran 2 neutrals. so the question is why does the first one go bad?
I think that when the GFCI 2 has an appliance plugged in, then the current on the neutral is going through the neutral line screw on GFCI 1 and the hot side of GFCI 1 has nothing thus wearing on the GFCI?
My options are to figure the basic principal of this out and fix it, or to simply pull a new neutral through the conduit, and completely separating the circuits.
Another thought is:
Does the length of the "sharing point" matter for the GFCI neutrals? If i was to take the neutrals off the GFCI and simply wire nut them 12" back with a pigtail, would path of least resistance totally bypass GFCI 1? because technicall all neutrals are connected, so at some point the actual connection or "splitting point" matters
Not a big deal, just wondering, I will be pulling a second Neutral.
I think that when the GFCI 2 has an appliance plugged in, then the current on the neutral is going through the neutral line screw on GFCI 1 and the hot side of GFCI 1 has nothing thus wearing on the GFCI?
My options are to figure the basic principal of this out and fix it, or to simply pull a new neutral through the conduit, and completely separating the circuits.
Another thought is:
Does the length of the "sharing point" matter for the GFCI neutrals? If i was to take the neutrals off the GFCI and simply wire nut them 12" back with a pigtail, would path of least resistance totally bypass GFCI 1? because technicall all neutrals are connected, so at some point the actual connection or "splitting point" matters
Not a big deal, just wondering, I will be pulling a second Neutral.