GFCI other then dwellings

Status
Not open for further replies.

charlie

Senior Member
Location
Indianapolis
Re: GFCI other then dwellings

Sorry, 210.8(B) from the 2002 NEC.

(B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1), (2), and (3) shall have ground-fault circuit-interrupter protection for personnel:
(1) Bathrooms
(2) Rooftops
Exception: Receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with the applicable provisions of Article 426.
(3) Kitchens
 

gardiner

Senior Member
Location
Canada
Re: GFCI other then dwellings

It will depend how the inspector defines kitchens the NEC doesn't seem to do it so it is up to him as what he considers a kitchen. In the majority of jurisdictions that my company has supplied refreshment stands the inspectors has asked they betreated as kitchens. If there is a sink, a coffeemaker or microwave then they tend to call it a kitchen or anywhere food may be perpared.

[ March 04, 2003, 03:22 PM: Message edited by: gardiner ]
 

charlie

Senior Member
Location
Indianapolis
Re: GFCI other then dwellings

You know, it is interesting that everyone knew what a bathroom was until GFCI's were required in them. At close to $50 a pop back then, no one knew what a bathroom was anymore. A strange thing happened; a definition was made so everyone knew what a bathroom was. Now . . . :roll:
 