GFCI outdoors 225 and 210.52

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
My question is GFCI protection required in this situation. I can't find what category this fits or maybe im trying to hard to fit it. IMO opinion I think all of these circuits need GFCI protection but i cannot find it in code. Help please!

Outdoor100amp Service disconnect/panel placed on an outdoor light pole. The 4 circuits feed under a parking lot about 60 ft to the ATM pad, 30amp ATM power direct wire, 2 Light poles controlled by photo cell, and some flood lights around the machine, router power, surge suppressor
 

jap

Senior Member
Occupation
Electrician
My question is GFCI protection required in this situation. I can't find what category this fits or maybe im trying to hard to fit it. IMO opinion I think all of these circuits need GFCI protection but i cannot find it in code. Help please!

Outdoor100amp Service disconnect/panel placed on an outdoor light pole. The 4 circuits feed under a parking lot about 60 ft to the ATM pad, 30amp ATM power direct wire, 2 Light poles controlled by photo cell, and some flood lights around the machine, router power, surge suppressor

I on the other hand don't think any of this requires GFI protection, and, if you do put in a GFI circuit for that ATM, and, I'm the one using it when it trips, I'm not moving until you show up to reset it.

I don't care how many horns are honkin,,,,, :)


JAP>
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I on the other hand don't think any of this requires GFI protection, and, if you do put in a GFI circuit for that ATM, and, I'm the one using it when it trips, I'm not moving until you show up to reset it.

I don't care how many horns are honkin,,,,, :)


JAP>
I was just thinking outdoors with people constantly touching it that there may be shock potential. I guess I am pounding the square peg in round hole
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with jap. I inow od no requirement for GFCI.
With hardwired equipment and proper grounding the need for GFCI is greatly diminished.
 

jap

Senior Member
Occupation
Electrician
I was just thinking outdoors with people constantly touching it that there may be shock potential. I guess I am pounding the square peg in round hole

You're not too far off base,,,, I know I hugged my new washer and dryer for at least 3 days straight after exhausting every attempt at reviving my old worn out units,,,,....

JAP>
 

cadpoint

Senior Member
Location
Durham, NC
An Off thread response

51eSo1zQ0cL._SX427_BO1,204,203,200_.jpg

Major Appliances (FIX-IT-YOURSELF)​

An Amazon Link

It's saved me many a time, and at least helped me with troubleshooting. A great addition to the house library, but JMO!

You're not too far off base,,,, I know I hugged my new washer and dryer for at least 3 days straight after exhausting every
attempt at reviving my old worn out units,,,,....

Group Hugs - Well practiced here at the house. Appliance hunging not so much :ROFLMAO:
 