Re: GFCI outlets
210.8(A) and 210.8(A)(6)
All of the receptacles that are installed to serve the contertops in kitchens have to be installed with ground-fault circuit interrupter protection. The code does not specify which receptacles have to be the actual GFCIs. They could be protected by a GFCI breaker.