GFCI problems
p051981
Houston, Texas
Hey yall, I know im probably in the wrong forum. I was at work today and i ran into a small problem. Someone ran a multiwire circuit feeding two GFCI. Each one has seperate hots but they are sharing a neutral. When i arrive at the house, both GFCI was trip. I reset the left GFCI and as soon as i pushed the reset on the right one (by they way they are side by side) they both tripped. I took the load side of the GFCI off and the problem didnt go away. Can a GFCI share a neutral or are they require separate neutrals?
Yes,
You must make a connection with the neutral on the line side of the 1st gfci.
Then go to the next gfci. You don't use the load side on the first one.
Or make a splice on the neutral in the j-box at the first gfci
If you use a dp GFCI breaker then the circuit will work fine.
Also as Buck mentioned the line can share the gfci at the receptacle but the loads must be separate.
A MWBC feeding two GFIs with downstream loads will not work.
As soon as a load is introduced, the GFIs will sense an imbalance and open the circuit.
You must either seperate the neutrals...
Or install a 2-pole GFI breaker,
Just pigtail the left gfci to black circuit to the line side only then pigtail the right gfci to red circuit to the line side only .This will give you 2 available circuits. Dont forget the ground wire if available. You will only have trouble trying to feed thru with a 3 wire ,not on the line in only connection.