ShauwnC
- Fairfax virginia
I am currently having a debate and want to know what article applies to recessed lights above a regular bath tub and wether they require GFCI protection or not. Any help would be greatly appreciated.
The NEC does not require GFCI protection for this application. It's a common misconception that it's a code requirement.
You are correct about the manufacturer's instructions, but that is one can light with that restriction. There are many others that do not have that requirement in the instructions.I'm going to have to DISagree in part with electricmanscott and iwire. If this is in a park trailer or if the manufacturer instructions say so and that tub has a 'shower head' like most do, then yes. 2014 NEC Park trailers 552.54(B)
Manufacturer's Instructions NEC 110.3(B)
Here is a shower light by Kohler that requires gfci protection in its instructions.
http://www.us.kohler.com/onlinecatalog/pdf/1015878_4.pdf
The park trailer reference is a narrow one. Bathrooms in those things are smaller than a phone booth.
A tub by another name is a different kind of wet as far as the NEC defines it.By the way, I forgot to mention the 'hot' tub. It is still a tub. ;-) NEC 680.43(B)(1)
And I will DISagree right back at you. :happyyes: The OP's question did not ask if it was ever required. It was more generic. And speaking in generic terms, the application described does not, by itself, require GFCI. :happyno:I'm going to have to DISagree in part with electricmanscott and iwire.