Hello All,
I've got this safety inspector who's thick headed and won't listen. He has experience with OSHA and I heard has attended OSHA forums/classes etc. All I want is an answer from someone who really knows!
This is the situation:
I am the Electrical Foreman at a renovation of a sewage treatment plant in NYC. I provided a temp. panel consisting of 1P, SQ. D., 20A, QO, Class A, Ground-fault Circuit Interrupter (GFCI) Breakers for temp. power. I installed drops out of the bottom of the panel as well as a couple of 80' long romex streamers consisting of 5 or 6 laundry drops and different intervals (all panel drops and streamers on separate circuits).
This inspector is telling me that OSHA requires 'portable' GFCI protector cord sets (such as the types seen here: http://www.aiwc.com/catalogsection/catalogpdfs/Cordset/gfci.pdf ) to be plugged in at the end of an extension cord (cords which are plugged into the laundry drops) or if a tool is to be plugged in at the laundry drop (without an extension cord) - which is already a GFCI (breaker) protected line.
Let me state that again... the temp. circuit is wired to a 20A Class A - GFCI Circuit Breaker. I am being told that any trade who wishes to utilize that temp. streamer must provide a portable GFCI cord set at the end of the cord.
His reasoning, though may sound logical and may just be true, is that the portable GFCI will trip faster than the GFCI breaker since the portable is closer to the person using the temp. line. Hence, it takes longer for the breaker to trip because of its distance from the person to the panel which is no more than 150' away.
Doing some research I found that OSHA requires the following:
EMPLOYER'S RESPONSIBILITY
OSHA ground-fault protection rules and regulations have been determined necessary and appropriate for employee safety and health. Therefore, it is the employer's responsibility to provide either: (a) ground-fault circuit interrupters on construction sites for receptacle outlets in use and not part of the permanent wiring of the building or structure; or (b) a scheduled and recorded assured equipment grounding conductor program on construction sites, covering all cord sets, receptacles which are not part of the permanent wiring of the building or structure, and equipment connected by cord and plug which are available for use or used by employees.
GROUND-FAULT CIRCUIT INTERRUPTERS
The employer is required to provide approved ground-fault circuit interrupters for all 120-volt, single-phase, 15- and 20-ampere receptacle outlets on construction sites which are not a part of the permanent wiring of the building or structure and which are in use by employees. Receptacles on the ends of extension cords are not part of the permanent wiring and, therefore, must be protected by GFCIs whether or not the extension cord is plugged into permanent wiring. These GFCIs monitor the current-to-the-load for leakage to ground. When this leakage exceeds 5 mA ? 1 mA, the GFCI interrupts the current. They are rated to trip quickly enough to prevent electrocution. This protection is required in addition to, not as a substitute for, the grounding requirements of OSHA safety and health rules and regulations, 29 CFR 1926. The requirements which employers must meet, if they choose the GFCI option, are stated in 29 CFR 1926.404(b)(1)(ii). (See appendix.)
It clearly states that I have provided GFCI protection on the receptacle outlets which are not part of the permanent bldg wiring. The 'ends of the extension cords'..., as it reads, 'must be protected by GFCIs' (which the breaker is) which I have accomplished.
The inspector states that there is an OSHA "Interpretation" to this stating that the portable GFCI device/cord must be at the outlet and that the breaker is not sufficient for personal protection and is meant for equipment protection. I said he is incorrect since a Class A device will trip when a fault to ground is 6mA or more.
So we are butting heads right now until I am satisfied with a documented OSHA Interpretation or response stating he is correct.
Is anyone familiar with such an OSHA Interpretation which states that a Class A GFCI Breaker is insufficient for protecting my streamers and that portable GFCI cord sets are needed at the tool, please enlighten me!!
Thanks,
Chris - Local #3 NYC
I've got this safety inspector who's thick headed and won't listen. He has experience with OSHA and I heard has attended OSHA forums/classes etc. All I want is an answer from someone who really knows!
This is the situation:
I am the Electrical Foreman at a renovation of a sewage treatment plant in NYC. I provided a temp. panel consisting of 1P, SQ. D., 20A, QO, Class A, Ground-fault Circuit Interrupter (GFCI) Breakers for temp. power. I installed drops out of the bottom of the panel as well as a couple of 80' long romex streamers consisting of 5 or 6 laundry drops and different intervals (all panel drops and streamers on separate circuits).
This inspector is telling me that OSHA requires 'portable' GFCI protector cord sets (such as the types seen here: http://www.aiwc.com/catalogsection/catalogpdfs/Cordset/gfci.pdf ) to be plugged in at the end of an extension cord (cords which are plugged into the laundry drops) or if a tool is to be plugged in at the laundry drop (without an extension cord) - which is already a GFCI (breaker) protected line.
Let me state that again... the temp. circuit is wired to a 20A Class A - GFCI Circuit Breaker. I am being told that any trade who wishes to utilize that temp. streamer must provide a portable GFCI cord set at the end of the cord.
His reasoning, though may sound logical and may just be true, is that the portable GFCI will trip faster than the GFCI breaker since the portable is closer to the person using the temp. line. Hence, it takes longer for the breaker to trip because of its distance from the person to the panel which is no more than 150' away.
Doing some research I found that OSHA requires the following:
EMPLOYER'S RESPONSIBILITY
OSHA ground-fault protection rules and regulations have been determined necessary and appropriate for employee safety and health. Therefore, it is the employer's responsibility to provide either: (a) ground-fault circuit interrupters on construction sites for receptacle outlets in use and not part of the permanent wiring of the building or structure; or (b) a scheduled and recorded assured equipment grounding conductor program on construction sites, covering all cord sets, receptacles which are not part of the permanent wiring of the building or structure, and equipment connected by cord and plug which are available for use or used by employees.
GROUND-FAULT CIRCUIT INTERRUPTERS
The employer is required to provide approved ground-fault circuit interrupters for all 120-volt, single-phase, 15- and 20-ampere receptacle outlets on construction sites which are not a part of the permanent wiring of the building or structure and which are in use by employees. Receptacles on the ends of extension cords are not part of the permanent wiring and, therefore, must be protected by GFCIs whether or not the extension cord is plugged into permanent wiring. These GFCIs monitor the current-to-the-load for leakage to ground. When this leakage exceeds 5 mA ? 1 mA, the GFCI interrupts the current. They are rated to trip quickly enough to prevent electrocution. This protection is required in addition to, not as a substitute for, the grounding requirements of OSHA safety and health rules and regulations, 29 CFR 1926. The requirements which employers must meet, if they choose the GFCI option, are stated in 29 CFR 1926.404(b)(1)(ii). (See appendix.)
It clearly states that I have provided GFCI protection on the receptacle outlets which are not part of the permanent bldg wiring. The 'ends of the extension cords'..., as it reads, 'must be protected by GFCIs' (which the breaker is) which I have accomplished.
The inspector states that there is an OSHA "Interpretation" to this stating that the portable GFCI device/cord must be at the outlet and that the breaker is not sufficient for personal protection and is meant for equipment protection. I said he is incorrect since a Class A device will trip when a fault to ground is 6mA or more.
So we are butting heads right now until I am satisfied with a documented OSHA Interpretation or response stating he is correct.
Is anyone familiar with such an OSHA Interpretation which states that a Class A GFCI Breaker is insufficient for protecting my streamers and that portable GFCI cord sets are needed at the tool, please enlighten me!!
Thanks,
Chris - Local #3 NYC