I am looking at the NEC 210.8 (A)(7) which requires all receptacles installed in dwelling units within 6 ft of the outside edge of a sink to have GFCI protection. However, when I look in 210.8 (B) "other than dwelling units", I can find no reference to having GFCI protection within any distance of a sink, except in bathrooms. There is no reference to sinks anywhere.
So, I did a final inspection on 2 elementary schools. There is a sink in every classroom. Although I did require GFCI protection, I can't see in the code where it would be required. Also, I did a final on an optical shop that has three different areas that have sinks with receptacles located near by. Again, I required the GFCI protection, but after looking at the code, I'm wondering if the EC wanted to argue about being required to add GFCI protection in these locations, if I would have to change my position. None of these locations meets the specifications of a bathroom or a kitchen.
Opinions please. Thanks
So, I did a final inspection on 2 elementary schools. There is a sink in every classroom. Although I did require GFCI protection, I can't see in the code where it would be required. Also, I did a final on an optical shop that has three different areas that have sinks with receptacles located near by. Again, I required the GFCI protection, but after looking at the code, I'm wondering if the EC wanted to argue about being required to add GFCI protection in these locations, if I would have to change my position. None of these locations meets the specifications of a bathroom or a kitchen.