Chamuit Grumpy Old Man Location Texas Occupation Electrician Jan 24, 2011 #1 Is GF protection required for general service receptacles in a woodworking factory? The receptacles are to be used at assembly tables. I looked through 210.8 and Commetary Table 210.1 (2005) and didn' see anything.
Is GF protection required for general service receptacles in a woodworking factory? The receptacles are to be used at assembly tables. I looked through 210.8 and Commetary Table 210.1 (2005) and didn' see anything.
B Bea Senior Member Jan 25, 2011 #2 There are no requirements in 210.8(B) that would require them or in 502 or 503 whichever class the area is. Unless there are local amendments that would require GFCI protection it is not required.
There are no requirements in 210.8(B) that would require them or in 502 or 503 whichever class the area is. Unless there are local amendments that would require GFCI protection it is not required.
Chamuit Grumpy Old Man Location Texas Occupation Electrician Jan 25, 2011 #3 The area does not meet the requirements of 502. This came issue up with the city and NEMA 4X is not required.
The area does not meet the requirements of 502. This came issue up with the city and NEMA 4X is not required.