shortcircuit2
Senior Member
- Location
- South of Bawstin
Would a single-phase 240-volt, 30-amp receptacle outlet in an unfinished basement of a 24 unit multifamily dwelling building require GFCI protection under 210.8(B) of the 2017 Code?
210.8(A)(5) Unfinished portions or areas of the basement not intended
as habitable rooms
I like your interpretation. Although I think it could be interpreted that the basement is associated with the dwelling units.
I am curious as to why the new rule is only for 210.8(B) applications, "other than dwelling units", and not for dwelling units where there is an equal hazard probability...at least in the unfinished basement of a dwelling unit.
Well if you're now saying that the basement is part of the dwelling unit then that kind of changes what you stated in the OP. So if it is part of the unit then you're correct no GFCI protection is required under the 2017 NEC.
Unfinished areas of a basement are required to be gfci in a dwelling
Dwelling Unit. A single unit, providing complete and inde‐pendent living facilities for one or more persons, including
permanent provisions for living, sleeping, cooking, and sanita‐
tion.
What type of breaker or receptacle is available for 240V 30 amp circuits?
Doesn't it say 150v or less?
If you are using 240v, it's not required to have GFCI.
Would a single-phase 240-volt, 30-amp receptacle outlet in an unfinished basement of a 24 unit multifamily dwelling building require GFCI protection under 210.8(B) of the 2017 Code?
I find it hard to think of an electric clothes dryer in an unfinished basement of a 24 unit multifamily dwelling as being anything connected as part of any one of those dwelling units. Rather, the electric dryer is in the common area outside of the dwellings, i.e., in the "nondwelling" space of the building.So if one put a laundry room in said basement, do you need GFCI protection on 30 amp electric dryer receptacles?
In a dwelling I think it is clear you don't need GFCI protection, but in other then dwelling applications it depends on what you call unfinished or not intended as habitable rooms.
I agree it is not connected as a part of any one of the dwelling units.I find it hard to think of an electric clothes dryer in an unfinished basement of a 24 unit multifamily dwelling as being anything connected as part of any one of those dwelling units. Rather, the electric dryer is in the common area outside of the dwellings, i.e., in the "nondwelling" space of the building.
Now how do we determine what is "unfinished basement" which may or may not dictate the need for GFCI protection with the new change?
I agreeYet is kind of stupid that for the same situation in an unfinished basement of an actual dwelling would not require GFCI:roll:
I'd like to know what the justification was for some of the changes to 210.8.
Don't have my 2017 nearby at the moment, but I recall it saying unfinished basements or similar uninhabitable spaces or something like that.They added areas that are not "habitable" to clear that up...
I agree
People getting electrocuted.
...did the same manufacturers that pushed the AFCI's into code under questionable circumstances and that also would manufacture the majority of the GFCI's that would be used here...