gfci on protection on new portable generator Honda EB inverted 5000I. I question how this generator could safely have gfci protection on the outlets providing power. WHen testing continuity, my results where that the grounding conductor and ground where bonded together to the motor housing and other metal surfaces. Is this a safety issue for my employees or am i missing something in electrical theory. I am unsure if the generator is a separately derived system in which case 250.30 would apply. If not, will a neutral to case bond cause objectionable current on the frame of the generator. Will the OCPD open and clear a case to ground fault removing touch voltage?