Is gfci protection still working after going through a VFD or a line reactor ?
Is gfci protection still working after going through a VFD or a line reactor ?
Yes it is at the
input,
Most VFDs will trip GFCI breakers, it's a known issue based on the way a VFD functions and how GFCIs sense what it thinks is (or might be) a "ground fault" based on current flowing that does not return. If you have seen a VFD work on a GFCI breaker, it was luck...
But what is the application that needs a GFCI and a VFD? Pool or spa pump? If so, is it a single phase into a 3 phase VFD going to a hard wired pump?
Expanded GFCI requirements of 2017 and 2020 NEC might make this a bigger issue than it used to be. For most part will only effect cord and plug supplied equipment though.
That's why I asked. There was a thread in here some time ago where we all went off discussing this, turned out the OP was misinterpreting the term "short circuit and ground fault protection" used in the NEC as meaning GFCI (which is does not). But the more recent changes now DO require GFCI in places where it once did not, and pool and spa equipment is one of those.
I too doubt that a GFCI breaker feeding the line side of a VFD is going to detect and trip if there is a ground fault on the LOAD side of the VFD, because the AC-DC-AC conversion process is basically isolating the load side from the line side.The VFD may trip on an output ground fault, most do, but not at Class A GFCI levels.
The output of a VFD is _not_ isolated from the input. Any current flowing out of the VFD to ground must be present as residual current on the input. The rectification, filtering, and modulation don't change this. The electrons have to come from somewhere, and without something like a transformer, they come from the supply to the VFD.
What the rectification, filtering, and modulation do change is the frequency characteristics of the residual current, perhaps taking this current out of the frequency range detected by the GFCI (do normal GFCIs detect DC faults? what about 360 Hz faults?)
Also the PWM switching causes lots of capacitive leakage current which must be dealt with, and can trip the GFCI.