mstrlucky74
- NJ
I believe it's not required by code so why do guys install these breakers for temporary light stringers? I don't see it as requirement in specs either.
590.6(B) still applies to receptacle outlets, just those not covered in (A).Probably 590.6(B) applies to temporary lighting outlets.
Temp lighting is not directly required to have GFCI protection, if supplied through a receptacle then the receptacle is what kicks in GFCI protection requirements.
590.4(D) Receptacles.
(1) All Receptacles. All receptacles shall be of the grounding
type. Unless installed in a continuous metal raceway
that qualifies as an equipment grounding conductor in accordance
with 250.118 or a continuous metal-covered cable
with 250.118, all branch circuits shall include a
separate equipment grounding conductor, and all receptacles
shall be electrically connected to the equipment
grounding conductor(s). Receptacles on construction sites
shall not be installed on any branch circuit that supplies
temporary lighting.
SECTION 590.6
Section 590.6 – Add an Exception after the first paragraph, to read as follows:
Exception: Temporary wiring installations that are accessible to the public and used to supply
temporary power for illumination of outdoor areas during construction, remodeling, maintenance,
repair, or demolition of buildings, structures, equipment, or similar activities shall comply with all other
requirements of this code for permanent wiring and shall be provided with ground-fault protection for
personnel.
In NYC temp power for lighting accessible to the public requires GFCI protection.
Not a bad idea, I wonder how that works out in practice?
We certainly can pick apart the wording here.For sure if you plug in say a light stand that would be from a GFCI receptacle
But we cannot tie receptacles into lighting circuits on construction sites.
For sure we can pick apart the wording but I think we can see the intent here.
Certainly out of reach to the public means it is not accessible to the public? Temporary lighting for an outdoor event but all the lighting is 20+ feet off the ground or at least in non public access locations - don't make any sense to me to require GFCI on that one. Temp lights hung at or below 8 feet in public access spaces - I can understand. Permanent lighting at or below 8 feet I can even understand in some places, especially if alcohol is consumed at the location in question.In NYC temp power for lighting accessible to the public requires GFCI protection.
It seems to work as long as water getting into the system isn't an issue.
I was not issuing a challenge.
To me this goes right back to what Ethan said in the stock / labor splitting thread. It is just internet nit picking, in practice it seems no one is having the difficulties you bring up.
So sidewalk bridge lighting etc., but not within the construction side though correct?
SECTION 590.8
Section 590.8 – Add a new section 590.8 to read as follows:
590.8 Sidewalk Shed Lighting. All sidewalk shed lighting installations shall comply with the following
conditions in addition to all other relevant provisions of this code:
(1) Such lighting shall be installed in a metal raceway approved for outdoor use.
(2) All junction boxes shall be suitable for damp or wet locations.
(3) A minimum wire size of 12 AWG shall be used for the installation.
(4) All fixtures shall be suitable for outdoor locations.
(5) Ground-Fault Circuit Interrupter (GFCI) protection is required on receptacles and lighting.
(6) The installation shall be properly grounded and bonded.
(7) The panel supplying power to the sidewalk shed lighting shall have a directory that clearly indicates
which circuit is being used to supply power.