Under the 2017 NEC is there a code reference that requires a 240v 30 or 50 amp receptacle on the outside of a single family dwelling to have GFCI protection ?
2017 if it were other than dwellings would require GFCI. Only 125 volt 15 and 20 amp receptacles are mentioned for the general 210.8 requirements in dwellings anyway.