C celticwatersbjc New member Location Hampton, VA USA Aug 24, 2011 #1 Is a GFCI protected receptacle required for a drinking fountain, if the fountain's flexible cord is plugged into that receptacle?
Is a GFCI protected receptacle required for a drinking fountain, if the fountain's flexible cord is plugged into that receptacle?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Aug 24, 2011 #2 422.52 Electric Drinking Fountains. Electric drinking fountains shall be protected with ground-fault circuit-interrupter protection.
422.52 Electric Drinking Fountains. Electric drinking fountains shall be protected with ground-fault circuit-interrupter protection.