ShockedMonkey
Member
- Location
- North SF Bay Area, CA
I have a GFCI receptacle and outlets fed on the load side (as well as a garage on the same 20 amp circuit) that a tester won't trip, don't know why.
Details:
20 amp 120 vac circuit off of older service, with a cold water ground to the first GFCI outlet (GFCI 'A' let's say.)
Another 3 receptacles are on load side, as well as a 20amp 120vac single-breaker box in garage. The breaker box has an isolated neutral bar and can grounded ground bus bar (unsure if it has a ufer, or anything and the "installer" has all kinds of hokey-non-sparky creations :roll:
Additional GFCI receptacles on the load side of the garage breaker trip via tester.
GFCI-A is good and will trip via it's 'test' button. It will also trip if I jump the isolated neutral bar with the ground bar in garage.
I thought it was something wonky at the garage, but I lifted the wires off all the bars to isolate it out of the circuit and GFCI still won't trip via tester.
GFCI tester works and trips other GFCI's in house that have a ground (old house not all have bare-wire.)
Any ideas why I can't get the tester to trip any outlets on GFCI-A's load side? I've only had a tester not trip a GFCI, if it didn't have an ECG.
Thanks
Details:
20 amp 120 vac circuit off of older service, with a cold water ground to the first GFCI outlet (GFCI 'A' let's say.)
Another 3 receptacles are on load side, as well as a 20amp 120vac single-breaker box in garage. The breaker box has an isolated neutral bar and can grounded ground bus bar (unsure if it has a ufer, or anything and the "installer" has all kinds of hokey-non-sparky creations :roll:
Additional GFCI receptacles on the load side of the garage breaker trip via tester.
GFCI-A is good and will trip via it's 'test' button. It will also trip if I jump the isolated neutral bar with the ground bar in garage.
I thought it was something wonky at the garage, but I lifted the wires off all the bars to isolate it out of the circuit and GFCI still won't trip via tester.
GFCI tester works and trips other GFCI's in house that have a ground (old house not all have bare-wire.)
Any ideas why I can't get the tester to trip any outlets on GFCI-A's load side? I've only had a tester not trip a GFCI, if it didn't have an ECG.
Thanks